Complete Circuit Flushing Procedure with Power Flush 17550

STEP 65
All refrigerant must be recovered from the system
before flushing.
STEP 66
The 17550 power flush unit uses shop air to atomize
the flushing solvent and a pulsing action to scrub
residue and contaminants out of components.
Fill the flushing reservoir 3/4 full with approved New
Holland flushing solvent. Do not overfill the
reservoir or you will restrict the pulsing action of
the unit.
STEP 67
Remove the receiver-dr ier and join the hoses
together with an adapter hose. Discard the receiver-
drier.
STEP 68
Remove the ther mal expansion valve and use
adapters to connect the hose lines to the evaporator.
Section 50 - Climate Control - Chapter 2
50-2-41