Thermal Expansion Valve Testing - New Holland T8010 Manual

Hide thumbs Also See for T8010:
Table of Contents

Advertisement

IMPORTANT: The following test is performed with the thermal expansion valve mounted in the system. No repair
or adjustment is recommended for the valve.
STEP 160
See ACCESSING THE HVAC BOX, page 90.
STEP 161
Disconnect the low pressure cutout switch. Install a
jumper wire across the harness leads.
STEP 162
Start the tractor and run the engine at 1500 RPM.
Turn blower speed control to maximum position,
temperature control valve fully clockwise, ATC switch
to DEFOG/DEFROST or Standard A/C switch to ON,
and check the low pressure gauge reading.
Compare the gauge readings to the Temperature/
Pressure chart for your ambient temperature and
humidity.
STEP 163
Remove thermal insulation tape from top of valve.
Use the palm of your hand to warm the expansion
valve and watch the low pressure gauge.
The valve will open and pressure should rise.
STEP 164
Use ice to cool the expansion valve and watch the
low pressure gauge.
Within seconds, the expansion valve will close and
the pressure must drop at the low pressure gauge.
STEP 165
If there is little or no change at low pressure gauge,
the thermal expansion valve must be replaced.
Section 50 - Climate Control - Chapter 2

THERMAL EXPANSION VALVE TESTING

Standard HVAC Box Shown
50-2-92