Table 2-1. Space Requirements - Tekelec T1000 Hardware Manual

Tekelec 1000 application server hardware manual
Table of Contents

Advertisement

Lighting
Adequate lighting should be provided in the room where the equipment is to be
located. Lighting fixtures must be far enough from the equipment and cables to
prevent heat damage and to allow safe access to equipment and cables.
Earthquake Resistance
All Tekelec system configurations are designed to assure that the system remains
operational during and after an earthquake, even when the system is located on
the upper floors of a zone 4 central office.
Space Requirements
Provide space as described in Table 2-1. These space requirements provide for
Tekelec equipment installed in a 23-inch heavy-duty frame, which measures 7 feet
high. Separator panels and end panels add to the width of multiple frame
systems.
Table 2-1.
Building Area
Halls
Frame location
Side aisles
Front and rear access
Side access
In addition, when planning the installation, be sure to take into account spare
hardware storage, modems, terminals, printers, cross connect panels, and all
other items that might require space in a system.
910-0095-001 Revision J November 2007
Space Requirements
Dimensions
4.5 feet wide by 8 feet
tall
(1.4 meters wide by
2.4 meters tall)
30 inches wide by 24
inches deep
(76.2 cm wide by 60.96
cm deep)
4 feet (1.2 meters)
3 feet 6 inches
(107 cm)
12 inches (31 cm)
Pre-Installation Site Requirements
Notes
To provide a clear, uncluttered route for
moving equipment between the
loading/receiving dock and the planned
system location
Floor area recommended for one Tekelec frame
(multiply by the number of frames listed on the
Initial Sales Order)
Total area per frame = 720 square inches (5.0
square feet)
(0.465 square meters)
To allow maneuvering frames into place and
provide ample work space around the
equipment
From walls or other frames
From walls or other frames