Inspect the four # 6-32 pan-head screws inserted in the cover standoffs for
enough clearance (approximately 1/4 inch) to slide the disk mounting bracket
over the large keyholes slots in the bracket. Add any missing screws or loosen
screws if necessary. See Figure 7-12.
13.
Do one of the following:
• If this procedure is being performed to replace a failed hard disk drive, do
both of the following:
— Note the position label attached to the failed hard disk drive assembly.
— Ensure that the jumper settings of the replacement hard disk drive
910-0095-001 Revision J November 2007
Select the matching label ("A" or "C") from the contents of the
shipping container in which the replacement hard disk drive assembly
was received, and apply it to the bracket holding the hard disk drive.
Figure 7-12 shows where the labels should be applied.
match the jumper settings of the failed hard disk drive. For example, if
the failed hard disk drive jumper settings are set to Master, ensure that
the replacement hard disk drive jumper settings are also set to Master.
Jumper settings may differ for different manufacturers. Figure 7-13
shows where the jumper pins are located and where the jumper
settings are shown.