Next, replace the desired FRU using one of the following procedures:
• Procedure 7-9, "Replace a Fan Assembly," on page 7-20
• Procedure 7-10, "Replace a Hard Disk Drive Assembly," on page 7-24
• Procedure 7-11, "Replace a Removable Media Disk Drive Assembly," on page
7-34
• Procedure 7-12, "Replace a PCI Card," on page 7-37
When the desired FRU has been replaced, perform Procedure 7-5, "Slide T1000 AS
Chassis Back into Frame," on page 7-9.
How to Slide T1000 AS Chassis Back into Frame
Perform the procedure in this section to slide the T1000 AS chassis back into the
frame if one of the following FRUs was accessed by sliding the T1000 AS chassis
out of the frame:
• Fan assemblies
• Hard disk drive assemblies
• Removable media disk drive assemblies
• PCI cards
Procedure 7-5.
WARNING:
when working on electronic components.
1.
From the front of the frame, simultaneously press the round release buttons
and slowly push the chassis into the frame while observing the cables to avoid
binding or stretching.
NOTE: When the chassis stops moving, the front of the T1000 AS should
be slightly recessed to allow clearance of the handles behind the frame door
when closed.
2.
Adjust the chassis retention brackets on the front of the T1000 AS chassis to
contact the frame adapter brackets when the chassis is positioned correctly in
the frame.
3.
Secure the chassis with one # 12-24 screw in the chassis retention brackets on
each side.
4.
This procedure is complete.
910-0095-001 Revision J November 2007
Slide T1000 AS Chassis Back into Frame
Always wear an ESD wrist strap grounded to the bench or frame
How to Access T1000 AS FRUs
7-9