Procedure 6-5.
1.
Connect one end of the logic ground cable with the 15-pin connector to the
port labeled "Logic Ground" at the rear of the T1000 AS chassis. This cable
does not need any special preparation and can be used as delivered with the
server.
2.
Connect the other end of the cable to one of the screws on the logic ground
terminal strip at the top right side of the frame. Do this for each server. See
Figure 6-5 on page 6-10.
3.
This procedure is complete.
Next, go to "How to Verify the Ground in a DC Environment" on page 6-11.
How to Verify the Ground in a DC Environment
After all frame components and all frame and logic ground cables are installed,
the hardware tester must verify the frame and logic grounds. Power-up the frame
using the procedure described in "How to Power Up" on page 6-14. Then, use the
multi-meter to test the isolated continuous aisle ground at the position show in
Figure 6-1 on page 6-5. The meter reading with the frame powered-up must be
less than 0.01 Amps.

How to Ground in an AC Environment

Perform the procedures in the following sections:
• For each server in the heavy duty frame, use the procedure in "How to
Connect Chassis Ground in an AC Environment" on page 6-11
• "How to Verify the Ground in an AC Environment" on page 6-12
How to Connect Chassis Ground in an AC Environment
Use the following procedure to ground the T1000 AS chassis to the rectifier
chassis in an AC environment.
Procedure 6-6.
1.
Attach the chassis cable into the back of the T1000 AS chassis. This cable can
be used as delivered with the server.
2.
Connect the other end of the cable to the back of the rectifier chassis.
910-0095-001 Revision J November 2007
How to Connect Frame Ground and Logic Ground
Connect Logic Ground: T1000 AS Logic Ground Port
to Logic Ground Terminal Strip
Connect Chassis Ground: T1000 AS Chassis to
Ground on Rectifier
6-11