Figure 6-2. Frame Ground Cable Attachment Locations In Dc Environment - Tekelec T1000 Hardware Manual

Tekelec 1000 application server hardware manual
Table of Contents

Advertisement

How to Connect Frame Ground and Logic Ground
Figure 6-2. Frame Ground Cable Attachment Locations in
12-24 Phillips head
screw with
captive star washer
(typical)
NOTE 1: Main Ground: 1/0 cable from the frame ground to the PANI "I"
(isolated) section of the ground window.
NOTE 2: Frame Ground: A cable #6 AWG from a frame is H-tapped into a
1/0 cable and terminates on the "I" section of the ground window. If no
ground window exists, the customer will designate the termination point.
NOTE 3: The size of the cable is determined by the overall length of the
cable run. Refer to the Site File Book.
7.
This procedure is complete.
Next, go to Procedure 6-3, "Connect T1000 AS Chassis Ground: T1000 AS Chassis
to Frame," on page 6-7.
6-6
DC Environment
Frame Ground To Tap
To PANI Isolated
#6AWG
Frame Ground
CHASSIS
GND
CLK
USB
A
B
Cable must fill and
be visible
in lug window
Frame Rear
Frame Ground
L o g i c G r o u n d
Ground strap
T e r m i n a l S t r i p
1
LOGIC GND
PWR B
PWR A
SERIAL
VGA
910-0095-001 Revision J November 2007
03_ts_frame_logic-gnd