Figure 6-4. Logic Ground Cable Routes

Ground window
Producers
Absorbers
P A N I
NOTE: This figure shows the maximum configuration of five servers in
the frame. For more complete information about the configuration used by
the application, refer to the
3.
Apply the 145C cable tag (see Figure 6-5 on page 6-10) to both ends of the logic
ground cable. Also, apply the "Do Not Disconnect" tag to both ends of the
logic ground cable.
910-0095-001 Revision J November 2007
How to Connect Frame Ground and Logic Ground
Neutral
Isolated
Clamp amp meter
test area
Bracket*
TekServer Frame
Logic ground
DC assembly
A reading of 0.01 amps is acceptable
a higher reading is not acceptable
To Ground Window
1/0AWG
(cable rack horns)
on brackets
Bracket*
Logic gnd
Frame 1
Breaker
panels
A
B
C
D
E
03_ts_system_logicgnd
drawing.
* = Brackets
as required
Logic gnd
6-9