Figure 6-1. Frame Ground Cable Routes In Dc Environment - Tekelec T1000 Hardware Manual

Tekelec 1000 application server hardware manual
Table of Contents

Advertisement

Figure 6-1. Frame Ground Cable Routes in DC Environment

Ground window
Producers
Absorbers
P A N I
Continous
aisle ground
NOTE: This figure shows the maximum configuration of five servers in
the frame. For more complete information about the configuration used by
the application, refer to the
4.
Label all cables with "TO" and "FROM" location information.
Example: FROM T1000 AS frame ground, TO isolated main ground.
5.
Ensure that a bolt through any nut must show at least two threads beyond the
nut, but no more than four threads should be showing.
6.
Use the lacing cord to secure a "DO NOT DISCONNECT LEAD" tag at each
end of the cable, just beyond the lug. Apply the 145C cable tags to both ends of
the frame ground cable.
910-0095-001 Revision J November 2007
Neutral
Isolated
Clamp amp meter
test area
Bracket*
Branch
P/N 830-0715-03
7 foot frame gnd #6
(cable typical)
TekServer System
Frame Ground
How to Connect Frame Ground and Logic Ground
A reading of 0.01 amps is acceptable
a higher reading is not acceptable
To Ground Window
Htap
Bracket*
Frame 1
Rear View
A
B
C
D
E
03_ts_frame_gnd
DC assembly
drawing.
* = Brackets
(cable rack horns)
as required
1/0AWG
on brackets
Breaker
panels
6-5