Removing A T1600 Three-Phase Delta Ac Power Supply Cord - Juniper T1600 Hardware Manual

Core router
Hide thumbs Also See for T1600:
Table of Contents

Advertisement

Copyright © 2010, Juniper Networks, Inc.
the other power supply automatically assumes the entire electrical load for the router.
If you have only one power supply, you must power off the system before removing the
AC power supply cord.
Removing a T1600 Three-Phase Delta AC Power Supply Cord on page 287
1.
Installing a T1600 Three-Phase Delta AC Power Supply Cord on page 289
2.

Removing a T1600 Three-Phase Delta AC Power Supply Cord

To remove a three-phase delta AC power supply cord:
Switch off the customer site circuit breakers to the power supply being removed. Make
1.
sure that the voltage across the AC power source cord is 0 V and that there is no
chance that the cord might become active during the removal process.
Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect
2.
the strap to one of the ESD points on the chassis.
Switch the power switch on the power supply faceplate to the standby position.
3.
NOTE: After powering off a power supply, wait at least 60 seconds before
turning it back on.
Remove the ESD grounding strap from the ESD point on the chassis, and attach it to
4.
an approved site ESD grounding point. See the instructions for your site.
Disconnect the AC power cord (see Figure 170 on page 287 from the power source.
5.
Figure 170: Three-Phase Delta AC Power Supply
Remove the ESD grounding strap from the approved site ESD grounding point. See
6.
the instructions for your site. Reconnect the strap to one of the ESD points on the
chassis.
Using a number 2 Phillips (+) screwdriver, loosen the two screws on the door of the
7.
metal wiring compartment that protects the AC terminal block.
Open the door of the metal wiring compartment.
8.
Chapter 17: Replacing T1600 Router Hardware Components