General Site Guidelines

Copyright © 2018, Juniper Networks, Inc.
Table 61: Router Environmental Specifications (continued)
Description
Temperature
Seismic
Maximum thermal output
NOTE:
Install the router only in restricted areas, such as dedicated equipment
rooms and equipment closets, in accordance with Articles 110-16, 110-17, and
110-18 of the National Electrical Code, ANSI/NFPA 70.
Routine Maintenance Procedures for the T4000 Router on page 331
General Safety Guidelines and Warnings on page 393
Qualified Personnel Warning on page 396
Restricted Access Warning on page 402
Efficient device operation requires proper site planning and maintenance and proper
layout of the equipment, rack or cabinet (if used), and wiring closet.
To plan and create an acceptable operating environment for your device and prevent
environmentally caused equipment failures:
Keep the area around the chassis free from dust and conductive material, such as
metal flakes.
Follow prescribed airflow guidelines to ensure that the cooling system functions properly
and that exhaust from other equipment does not blow into the intake vents of the
device.
Follow the prescribed electrostatic discharge (ESD) prevention procedures to prevent
damaging the equipment. Static discharge can cause components to fail completely
or intermittently over time.
Install the device in a secure area, so that only authorized personnel can access the
device.
Chapter 9: Planning and Preparing the Site
Value
Normal operation ensured in temperature range of 32°F (0°C) to
104°F (40°C)
Nonoperating storage temperature in shipping : –40°F (–40°C) to
158°F (70°C)
Designed to meet Telcordia Technologies Zone 4 earthquake
requirements
DC power: 33583.6 BTU/hour (9840 W W)