Figure 225: Disconnecting The Ac Power Cord From A Three-Phase Wye Ac Power; Supply - Juniper T640 Hardware Manual

Core router
Hide thumbs Also See for T640:
Table of Contents

Advertisement

T640 Core Router Hardware Guide
366
Using a number 2 Phillips (+) screwdriver, unscrew the two screws on the metal cover
7.
protecting the AC terminal block.
Disconnect the wires from the AC terminal block and grounding point on the
8.
three-phase wye AC power supply
remove each wire from the grounding point or input terminal.
NOTE:
The terminal connections have either slotted screws or hex screws.
Use a 1/4-in. slotted screwdriver for the slotted screws. Use a 5/32-in
(4-mm) Allen wrench for the 5/16-in hex screws.
Remove the wire labeled
a.
Remove the wire labeled
b.
Remove the wire labeled
c.
Remove the wire labeled
d.
Remove the wire labeled
e.
Figure 225: Disconnecting the AC Power Cord from a Three-Phase Wye
AC Power Supply
Loosen the plastic cable tie fastening the AC power cord to the power supply.
9.
Loosen and remove the retaining nut from the AC power cord.
10.
Pull the AC power cord out of the metal wiring compartment.
11.
Carefully move the AC power cable out of the way.
12.
Loosen the captive screws on the lower corners of the power supply faceplate
13.
completely.
Twist the ejector handles on the upper corners of the faceplate counterclockwise to
14.
unseat the power supply.
Grasp the handle on the power supply faceplate and pull firmly. Slide it halfway out
15.
of the chassis (see
Figure 226 on page
(Figure 225 on page
N
from the
N
input terminal
from the
input terminal.
L3
L3
from the
input terminal.
L2
L2
from the
input terminal.
L1
L1
from the grounding point labeled
GND
L1
L2 L3
N
367).
Copyright © 2013, Juniper Networks, Inc.
366), loosen each screw, and
.
GND

Advertisement