Figure 187: Connecting A Power Cable To A Four-Input 240-A Dc Power - Juniper T640 Hardware Manual

Core router
Hide thumbs Also See for T640:
Table of Contents

Advertisement

Copyright © 2017, Juniper Networks, Inc.
Secure the cable lugs to the terminal studs, first with a washer, then with a nut (see
Figure 187 on page
371). Use a 7/16-in. (11 mm) nut driver to tighten the nut. Apply
between 23 lb-in. (2.6 Nm) and 25 lb-in. (2.8 Nm) of torque to each nut.
CAUTION:
You must use an appropriate torque-controlled tool to tighten
the nuts. Applying excessive torque damages the terminal studs and the
power supply. The absolute maximum torque that may be applied to this
nut is 45 lb-in. (5.0 Nm).

Figure 187: Connecting a Power Cable to a Four-Input 240-A DC Power

Supply
Cable lug
Locking
washer
Nut
Loosen the captive screws on the cable restraint on the right edge of the power supply
11.
faceplate.
Route the DC power cables through the cable restraint.
12.
Tighten the cable restraint captive screws to hold the power cables in place.
13.
Verify that the power cabling is correct, that the power cables do not touch or block
14.
access to other hardware components, and that they do not drape where people
could trip on them.
Chapter 29: Replacing Power System Components
Terminal studs
371