Supply; Removing The T640 Standard Cable Restraint From A Three-Input 240-Adc Power Supply; Installing The T640 Optional Cable Restraint On A Three-Input 240-Adc Power Supply - Juniper T640 Hardware Manual

Core router
Hide thumbs Also See for T640:
Table of Contents

Advertisement

T640 Core Router Hardware Guide
362
cable restraint (see
"Optional Cable Restraint on a Three-Input 240-A Power Supply"
on page
362) on each three-input 240-A DC power supply.
NOTE:
Before you remove a chassis from a rack or cabinet, you must remove
the optional cable restraint from the three-input 240-A DC power supply.
To replace the cable restraint on a three-input 240-A DC power supply, perform the
following tasks:
Removing the T640 Standard Cable Restraint from a Three-Input 240-A DC Power
Supply on page 362
Installing the T640 Optional Cable Restraint on a Three-Input 240-A DC Power
Supply on page 362
Removing the T640 Standard Cable Restraint from a Three-Input 240-A DC
Power Supply
The cable restraint is located on the right edge of the power supply faceplate. To remove
the standard cable restraint from a three-input 240-A DC power supply:
Loosen the captive screw on the standard cable restraint or captive screws on the
1.
optional cable restraint.
Remove the cable restraint from the power supply.
2.
Figure 180: Standard Cable Restraint on a Three-Input 240-A DC Power

Supply

Installing the T640 Optional Cable Restraint on a Three-Input 240-A DC Power
Supply
To install the optional cable restraint on a three-input 240-A DC power supply:
Align the two captive screws on the optional cable restraint with the two threaded
1.
holes located at the right edge of the power supply faceplate.
Copyright © 2017, Juniper Networks, Inc.