Juniper T640 Hardware Manual page 505

Core router
Hide thumbs Also See for T640:
Table of Contents

Advertisement

Table 95: T640 Cooling System Alarm Messages (continued)
Component
Alarm Type
Temperature
Red
sensors
Yellow
Solution
Copyright © 2017, Juniper Networks, Inc.
LCD Message
Temperature Hot
Sensor Failure
Temperature Warm
To troubleshoot the cooling system:
Place your hand near the exhaust vents at the rear of the chassis to determine whether
1.
the fans are pushing air out of the chassis.
If the red alarm LED on the craft interface lights, look at the craft interface display to
2.
find the source of the problem. The number of alarm conditions, as well as the source
of each alarm, appears on the screen.
Chapter 33: Troubleshooting Components
CLI Message
Alarm Condition
The chassis
Temperature Hot
temperature
exceeded the hot
temperature
threshold. If this
condition persists,
the router shuts
down.
Temperature sensor
A temperature
sensor failed.
failure
The chassis
Temperature Warm
temperature
exceeded the warm
temperature
threshold.
Solution
Verify that the
room
temperature is
within
acceptable
limits.
Verify that
there is
sufficient air
flow.
Verify that the
cooling system
in the chassis is
operating
properly.
Contact JTAC.
Verify that the
room
temperature is
within
acceptable
limits.
Verify that
there is
sufficient air
flow.
Verify that the
cooling system
in the chassis is
operating
properly.
471

Advertisement

Table of Contents
loading

Table of Contents