You must route the cables as marked to be able to replace the
clear plastic cover over the terminal studs.
Attach the positive (+) DC source power cable lugs to the
terminals on the left. Secure the cable lugs to the terminal studs, first with the
RTN 4
washers, then with the nuts. Using a 7/16-in. (11 mm) nut driver, tighten the nuts. Apply
between 23 lb-in. (2.6 Nm) and 25 lb-in. (2.8 Nm) of torque to each nut.
Replace the left cable restraint, and tighten the captive screw to hold the power cables
14.
for
,
,
RTN 0
RTN 1
RTN 3
Figure 72: Connecting Positive (+) DC Power Cables to RTN 2, RTN 5,
RTN 0, RTN 1, RTN 3, and RTN 4
Verify that the power cabling is correct, that the power cables are not touching or
15.
blocking access to router components, and that they do not drape where people could
trip on them.
Replace the clear plastic cover over the terminal studs on the faceplate.
16.
Tools and Parts Required to Provide Power to the T4000 Router on page 121
Connecting DC Power to the T4000 Router (Five 60-A Inputs) on page 126
Connecting DC Power to the T4000 Router (Four 60-A Inputs) on page 130
Connecting DC Power to the T4000 Router (Three 80-A DC Power Cables to Six 60-A
Inputs) on page 133
Powering On the T4000 Router on page 141
Configuring DC Power on a T4000 Router on page 148
Troubleshooting the T4000 Power System on page 204
T4000 DC Power Electrical Safety Guidelines on page 320
T4000 DC Power Cable and Lugs Specifications on page 341