2. If the server is installed at a level between 21U and 40U (*1): (*1 Judged based on the
level of the equipment top)
1300mm
800mm
Incorrect Operating Input Voltage Range for DC Input
Models
The Power Source Requirements section of the SPARC Enterprise T5140 and T5240 Site
Planning Guide contains tables that identify power specifications for various server
configurations. The operating input voltage range for DC input models indicated in each
table is incorrect. The correct value is as follows:
General Specifications(DC Input Models)
Operating input voltage range
(input voltage tolerance +/- 10%)
Also, the maximum operating input current and maximum operating input power indicated in
each table were the values at -48 VDC, not at -40VDC.
General Specifications(DC Input Models)
Maximum operating input current
Maximum operating input power
Rear-side clearance for service access
800mm
Equipment rack
1050mm
Front-side clearance for service access
1400mm
700mm
1400mm
Incorrect
–
-40
-75 VDC
Incorrect
At -40VDC: xx.x A
At -40VDC: xxxx.x W
Chapter 4
Correct
–
-48
-60 VDC
Correct
At -48VDC: xx.x A
At -48VDC: xxxx.x W
Documentation Errata
49