The SPARC Enterprise T5140 and T5240 servers require physical access from the top for
maintenance. Therefore, a stepladder may be required depending on which rack the server is
installed in. And it may be necessary to remove the server from the rack depending on the
component to be replaced.
The minimum clearance for service access varies depending on whether a stepladder is used.
Secure an appropriate clearance for service access before starting maintenance.
This section shows the minimum clearance for service access premised on the standard
maintenance work of our company. If this minimum clearance cannot be secured, contact our
field engineer.
No stepladder is required if this server is installed at the 20U level or lower. A stepladder is
required if it is installed at the 21U level or higher.
clearance for service access required for either server.
FIGURE 4-1
1. If the server is installed at the 20U level or lower (*1): (*1 Judged based on the level of
the equipment top)
48
SPARC Enterprise T5140 and T5240 Servers Product Notes • November 2012
Minimum Clearance for Service Access
Rear-side clearance for service access
Equipment rack
Front-side clearance for service access
1700mm
700mm
800mm
FIGURE 4-1
800mm
1050mm
800mm
shows the minimum