Fujitsu SPARC Enterprise T5440 Installation And Setup Manual

Hide thumbs Also See for SPARC Enterprise T5440:
Table of Contents

Advertisement

Advertisement

Table of Contents
loading

Summary of Contents for Fujitsu SPARC Enterprise T5440

  • Page 3 SPARC Enterprise T5440 Server Installation and Setup Guide Manual Code C120-E510-02EN Part No. 875-4388-11 July 2009, Revision A...
  • Page 4 Fujitsu Limited or Sun Microsystems, Inc., or any affiliate of either of them.
  • Page 5 L’ABSENCE DE CONTREFAÇON, SONT EXCLUES, DANS LA MESURE AUTORISÉE PAR LA LOI APPLICABLE. Sauf mention contraire expressément stipulée dans ce contrat, dans la mesure autorisée par la loi applicable, en aucun cas Fujitsu Limited, Sun Microsystems, Inc. ou l’une de leurs filiales ne sauraient être tenues responsables envers une quelconque partie tierce, sous quelque théorie juridique que ce soit, de tout manque à...
  • Page 7: Table Of Contents

    Contents Preface ix Preparing for Installation 1 About the SPARC Enterprise T5440 Server 1 Tools and Equipment Needed 2 Installation Overview 3 Optional Component Installation 5 Cabling Notes 5 About the Slide Rail Assembly About the Cable Management Arm 8...
  • Page 8 Log Into the Service Processor Using the Network Management Port Using the Service Processor for Common Operations 45 ▼ Power On the System 45 ▼ Connect to the System Console 47 SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 9 ▼ Perform a Normal System Initialization 47 Booting the Solaris Operating System 49 ▼ Boot the Solaris Operating System 49 ▼ Avoid Booting the Solaris Operating System at Start Up 50 ▼ Reset the System 50 ▼ Power Cycle the System 50 Updating the Firmware 53 Updating Service Processor and Server Firmware 53 Updating the Firmware 54...
  • Page 10 SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 11: Preface

    Use the product according to the instructions and information available in this manual. Keep this manual handy for further reference. Fujitsu makes every effort to prevent users and bystanders from being injured or from suffering damage to their property. Use the product according to this manual.
  • Page 12: Related Documentation

    SPARC Enterprise T5440 Server Server specifications for site planning C120-H029 Site Planning Guide SPARC Enterprise T5440 Server Detailed rackmounting, cabling, power on, C120-E510 Installation and Setup Guide and configuring information SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 13 Title Description Manual Code SPARC Enterprise T5440 Server How to run diagnostics to troubleshoot the C120-E512 Service Manual server, and how to remove and replace parts in the server SPARC Enterprise T5440 Server How to perform administrative tasks that C120-E511...
  • Page 14: Text Conventions

    These are called class options. Replace command-line To delete a file, type rm filename. variables with real names or values. * The settings on your browser might differ from these settings. SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 15: Conventions For Alert Messages

    Prompt Notations The following prompt notations are used in this manual. Shell Prompt Notations C shell machine-name% C shell superuser machine-name# Bourne shell and Korn shell Bourne shell and Korn shell superuser ILOM service processor -> ALOM compatibility shell sc> OpenBoot PROM firmware Conventions for Alert Messages This manual uses the following conventions to show alert messages, which are...
  • Page 16: Alert Messages In The Text

    Alert message example: Caution – The following tasks regarding this product and the optional products provided from Fujitsu should only be performed by a certified service engineer. Users must not perform these tasks. Incorrect operation of these tasks may cause malfunction.
  • Page 17 Always load equipment into a rack from the bottom up so that it will not become top-heavy and tip over. The SPARC Enterprise T5440 server weighs approximately 88 lb (40 kg). Two people are required to lift and mount this server into a rack enclosure when using the procedures in this document.
  • Page 18 Maintenance and inspections (repairing, and regular diagnosis and maintenance) ■ Caution – The following tasks regarding this product and the optional products provided from Fujitsu should only be performed by a certified service engineer. Users must not perform these tasks. Incorrect operation of these tasks may cause malfunction.
  • Page 19 Fujitsu Welcomes Your Comments If you have any comments or requests regarding this document, or if you find any unclear statements in the document, please state your points specifically on the form at the following URL. For Users in U.S.A., Canada, and Mexico: (https://download.computers.us.fujitsu.com/)
  • Page 20 (http://www.fujitsu.com/global/contact/computing/sparce_index.ht xviii SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 21: Preparing For Installation

    Electrostatic discharge precautions to “ESD Precautions” on page 11 prevent damage to equipment during the installation process About the SPARC Enterprise T5440 Server The SPARC Enterprise T5440 is a 4 rack unit (4U) server (FIGURE: SPARC Enterprise T5440 Server on page...
  • Page 22: Tools And Equipment Needed

    ASCII terminal ■ Workstation ■ Terminal server ■ Patch panel connected to a terminal server ■ Related Information “Safety Precautions” on page 10 ■ “ESD Precautions” on page 11 ■ SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 23: Installation Overview

    For more information, refer to the Integrated Lights Out Manager 3.0 Supplement for SPARC Enterprise T5440 Server. 6. Connect the data cables to the server, but do not connect the AC power cable yet.
  • Page 24 Solaris OS configuration procedure. 13. Install any required patches to the server. Refer to the SPARC Enterprise T5440 Server Product Notes for a list of required patches. 14. Load additional software from the Solaris media kit (optional).
  • Page 25: Optional Component Installation

    Network Management Port” on page 37. The service processor network management port uses an RJ-45 cable for a 10/100 BASE-T connection. This port does not support connections to Gigabit networks. See the SPARC Enterprise T5440 Server Overview Guide for more information. Preparing for Installation...
  • Page 26 SPARC Enterprise T5440 Server Site Planning Guide ■ “Safety Precautions” on page 10 ■ “About the Cable Management Arm” on page 8 ■ “Rear Panel Cable Connections Reference” on page 27 ■ SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 27: About The Slide Rail Assembly

    About the Slide Rail Assembly The rackmount kit has two slide rail assemblies, one for each side of the rack. Each slide rail assembly is marked LEFT or RIGHT. Each slide rail assembly consists of a three-section slide rail and a removable inner rail (FIGURE: Rackmount Kit Parts on page Rackmount Kit Parts...
  • Page 28: About The Cable Management Arm

    A cable management arm (CMA) attaches to the slide rails and the rear panel of the server. Route cables through the CMA brackets, securing the brackets with the hook-and-loop fasteners. SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 29: Rack Compatibility Requirements

    Cable Management Arm FIGURE: Related Information “Tools and Equipment Needed” on page 2 ■ “Cabling Notes” on page 5 ■ “About the Slide Rail Assembly” on page 7 ■ “Rack Compatibility Requirements” on page 9 ■ “Installing the Cable Management Arm (CMA)” on page 22 ■...
  • Page 30: Safety Precautions

    Caution – Always load equipment into a rack from the bottom up so that it will not become top-heavy and tip over. Caution – The SPARC Enterprise T5440 server weighs approximately 88 lb. (40 kg). Two people are required to lift and mount this server into a rack enclosure when using the procedures in this document.
  • Page 31: Esd Precautions

    Caution – When completing a two-person procedure, always communicate your intentions clearly before, during, and after each step to minimize confusion. Related Information SPARC Enterprise T5440 Server Safety and Compliance Guide ■ “ESD Precautions” on page 11 ■ ESD Precautions Electronic equipment is susceptible to damage by static electricity.
  • Page 32 SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 33: Installing The Sparc Enterprise T5440 Server

    Installing the SPARC Enterprise T5440 Server These topics provide instructions for installing the server into an equipment rack. Note – If your rackmount kit came with its own instructions, use the instructions in your rackmount kit instead of the instructions in this chapter. After performing the server installation, proceed to “Powering On the System”...
  • Page 34: Installing The Rack Slide Assembly

    FIGURE: Attaching the Inner Glides to the Chassis on page Note – Each inner rail is labeled “left” and “right.” Ensure you are attaching the inner rail to the correct side of the server. SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 35 4. Verify that all six locating pins are trapped in the keyed openings. 5. Repeat Steps 1 to 4 to install the remaining inner rail on the other side of the server. Installing the SPARC Enterprise T5440 Server...
  • Page 36: Determine Rackmount Location

    In a rack with three holes per rack unit, the server occupies 12 holes in height per rack column post. See FIGURE: Using the Rackmount Template on page Using the Rackmount Template FIGURE: Figure Legend Six mounting holes SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 37: Attach The Slide Rails To The Cabinet

    1. Before attaching the slide rails to the rack, fully collapse the inner slide assembly. Slide the inner glide all the way into the slide rail assembly. Release the spring-activated slide-rail lock. See FIGURE: Releasing the Slide Rail Lock on page Installing the SPARC Enterprise T5440 Server...
  • Page 38 Note – The rackmount kit includes both metric and standard fasteners. Use the fasteners appropriate for your cabinet. 5. Ensure each rail is fully recessed into its outer rail. 6. Move to the rear of the rack. SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 39: Installing The Server Into The Cabinet

    19 Verify proper server installation. “Verify Proper Slide-Rail Operation” on page 21 Related Information SPARC Enterprise T5440 Server Site Planning Guide ■ “Tools and Equipment Needed” on page 2 ■ “About the Slide Rail Assembly” on page 7 ■...
  • Page 40 The server locks in the extended service position. 4. Press the inner rail release buttons and slide the server all the way into the cabinet. See FIGURE: Slide the Server Into the Cabinet on page SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 41: Verify Proper Slide-Rail Operation

    To install or replace internal parts in the server, you must first remove the server from the rack. For the removal procedure, refer to the SPARC Enterprise T5440 Server Service Manual. Installing the SPARC Enterprise T5440 Server...
  • Page 42: Installing The Cable Management Arm (Cma)

    Before you begin, complete the following tasks: “Installing the Rack Slide Assembly” on page 14 ■ “Installing the Server Into the Cabinet” on page 19 ■ Do the following: SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 43: Attach The Cma

    “Attach the CMA Support Strut” on page 22 ■ 1. If necessary, slide the server back until it reaches the internal stops. 2. Fold the CMA as shown in FIGURE: Folding the CMA on page Folding the CMA FIGURE: Installing the SPARC Enterprise T5440 Server...
  • Page 44 Cable Management Arm on page 24). Slide the CMA into the end of the inner rail until the retaining pin snaps into place. Attaching the Cable Management Arm FIGURE: SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 45: Connecting The Server Cables

    FIGURE: Server Rear Panel Connections on page 28 for connector locations. Note – The cable and DB-9 RJ-45 adapters are for the host serial port, and not for the service processor serial management port. Installing the SPARC Enterprise T5440 Server...
  • Page 46: Connect The Service Processor Network Management Port

    Dynamic Host Configuration Protocol (DHCP) and allow connections using Solaris Secure Shell (SSH). You might need to modify these settings for your network. Instructions are given in “Powering On the System” on page SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 47: Connect The Ethernet Network Cables

    AC power. Rear Panel Cable Connections Reference FIGURE: Server Rear Panel Connections on page 28 for the locations of the ports on the SPARC Enterprise T5440 server. Installing the SPARC Enterprise T5440 Server...
  • Page 48 Note – You must follow the proper sequence when connecting cables to the server. Related Information “Cabling Notes” on page 5 ■ “Safety Precautions” on page 10 ■ “ESD Precautions” on page 11 ■ SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 49: Managing Cables With The Cma

    2. Verify the operation of the slide rails and CMA, and cable fasteners. Slide the server in and out of the cabinet to ensure that the server is operating smoothly, and that the cables are not binding or getting tangled. Installing the SPARC Enterprise T5440 Server...
  • Page 50 SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 51: Powering On The System

    Booting the Solaris OS, and configuring the “Booting the Solaris Operating System” on system to not boot into the Solaris OS. page 49 Related Information “Preparing for Installation” on page 1 ■ “Installing the SPARC Enterprise T5440 Server” on page 13 ■...
  • Page 52: Powering On The System For The First Time

    ■ Integrated Lights Out Manager 3.0 Concepts Guide ■ Integrated Lights Out Manager 3.0 Supplement for SPARC Enterprise T5440 Server ■ About the ILOM System Console When you power on the system, the boot process begins under the control of the Integrated Lights Out Manager (ILOM) system console.
  • Page 53: About The Ilom Service Processor

    Management Port” on page Related Information SPARC Enterprise T5440 Server Service Manual ■ Integrated Lights Out Manager 3.0 Supplement for SPARC Enterprise T5440 Server ■ “Rear Panel Cable Connections Reference” on page 27 ■ “Enabling the Service Processor Network Management Port” on page 37 ■...
  • Page 54 ILOM firmware. After a few minutes, the SP login prompt appears on the terminal device. The host is not initialized or powered on yet. SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 55 5. At the terminal device, log in to the SP as root with a password of changeme. XXXXXXXXXXXXXXXX login: root Password: changeme . . . -> After a brief delay, the SP prompt is displayed (->). At this point, there are many commands you can perform using the Integrated Lights Out Manager interface.
  • Page 56: Solaris Os Host Configuration Reference

    Accept the default date and time or change the values. root Password Enter the root password twice. This password is for the superuser account for the Solaris OS on this server. This password is not the SP password. SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 57: Enabling The Service Processor Network Management Port

    Related Information SPARC Enterprise T5440 Server Administration Guide. ■ “Rear Panel Cable Connections Reference” on page 27 ■ “Enabling the Service Processor Network Management Port” on page 37 ■ “Logging Into the Service Processor” on page 39 ■ “Using the Service Processor for Common Operations” on page 45 ■...
  • Page 58: Enable The Service Processor Network Management Port In A Network Using Dhcp

    1. After the service processor boots, access the ILOM CLI through the serial management port. See “Log Into the Service Processor Using the Network Management Port” on page SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 59: Logging Into The Service Processor

    Network Management Port” on page 44 Related Information “About the ILOM Service Processor” on page 33 ■ SPARC Enterprise T5440 Server Administration Guide ■ Integrated Lights Out Manager 3.0 Supplement for SPARC Enterprise T5440 Server ■ Powering On the System...
  • Page 60: Log Into The Service Processor Using The Serial Management Port

    2. Enter root for the login name followed by your password. hostname login: root Password: password (nothing displayed) Waiting for daemons to initialize... Daemons ready SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 61: Configure The Service Processor Network Management Port

    Note – For more information on configuring ILOM, refer to the Integrated Lights Out Manager 3.0 Supplement for SPARC Enterprise T5440 Server 1. Set these network parameters according to the specific details of your network configuration: /SP/network state –...
  • Page 62 Set 'pendingipnetmask' to '255.255.255.0' This example uses 255.255.255.0 to set the netmask. Your network environment subnet might require a different netmask. Use a netmask number most appropriate to your environment. SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 63 3. Use the show /SP/network command to verify that the parameters were set correctly. The following example shows parameters that have been set to convert a service processor from a dhcp configuration to a static configuration -> show /SP/network /SP/network Targets: Properties: commitpending = (Cannot show property)
  • Page 64: Log Into The Service Processor Using The Network Management Port

    % ssh root@xx.xxx.xx.x Are you sure you want to continue connecting (yes/no)? yes Password: password (nothing displayed) Waiting for daemons to initialize... Daemons ready Integrated Lights Out Manager Version 2.0.0.0 -> SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 65: Using The Service Processor For Common Operations

    -> prompt. Related Information “About the ILOM System Console” on page 32 ■ SPARC Enterprise T5440 Server Administration Guide ■ ▼ Power On the System 1. Perform the following steps to verify that there are no faults: a. Set the virtual keyswitch to diag mode so that POST will run in Service mode.
  • Page 66 2. Type the console escape sequence (by default #. (Hash-Period)) to return to the ILOM prompt. 3. Check the POST execution result with the following command: -> show /SP/faultmgmt -level all SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 67: Connect To The System Console

    Note – Depending on the configuration of ILOM, POST variables, and whether POST detected faults or not, the server might boot, or the system might remain at the ok prompt. If the system is at the ok prompt, type boot. 4.
  • Page 68 2007-12-14 16:45:28.824 0:1:0>Master set ACK for vbsc runpost command and spin... SPARC Enterprise T5440, No Keyboard OpenBoot 4.27.x, 3968 MB memory available, Serial #74409918. Ethernet address 0:14:4f:6f:67:be, Host ID: 846f67be. {0} ok SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 69: Booting The Solaris Operating System

    Related Information “Solaris OS Host Configuration Reference” on page 36 ■ SPARC Enterprise T5440 Server Administration Guide ■ ▼ Boot the Solaris Operating System 1. At the ok prompt, boot from the disk that contains the Solaris OS.
  • Page 70: Avoid Booting The Solaris Operating System At Start Up

    91 system services are now being stopped. Jun 12 19:46:57 wgs40-58 syslogd: going down on signal 15 svc.startd: The system is down. syncing file systems... done Program terminated r)eboot, o)k prompt, h)alt? SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 71 2. Switch from the system console prompt to the service processor console prompt by issuing the console escape sequence (by default, #. (Pound-Period)). ok #. -> 3. Using the ILOM CLI, type the stop /SYS command to perform a graceful shutdown of the system.
  • Page 72 For more information about configuring the server, refer to the SPARC Enterprise T5440 Server Administration Guide. For more information about adding optional components, refer to the SPARC Enterprise T5440 Server Service Manual. SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 73: Updating The Firmware

    Updating the Firmware This appendix provides instructions for updating SP firmware. Topic Links Updating both the server firmware and the “Updating Service Processor and Server ILOM firmware using the flashupdate Firmware” on page 53 command Restarting the service processor after “Updating the Firmware”...
  • Page 74: Updating The Firmware

    If the host is not powered off, type the stop /SYS command. -> stop /SYS 4. Verify that the keyswitch_state parameter is set to normal. -> set /SYS keyswitch_state=normal SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 75 5. Type the load command. The load command updates the service processor flash image and the host firmware. The load command requires the following information: IP address of a TFTP server on the network that can access the flash image ■...
  • Page 76 Starting system log daemon: syslogd and klogd. Starting periodic command scheduler: cron. Starting IPMI Stack..Done. Starting OpenBSD Secure Shell server: sshd. Starting Servicetags listener: stlistener. Starting FRU update program: frutool. hostname login: SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 77: Selecting A Boot Device

    Note – The serial management port is preconfigured as the default system console port. For more information, see the SPARC Enterprise T5440 Server Overview Guide. If you want to boot from a network, you must connect the network interface to the network.
  • Page 78 The show-devs command lists the system devices and displays the full path name of each PCI device. SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 79: Index

    Index Symbols configuring the network management port, 37 connecting to the system console, 47 #. escape sequence for system console, 51 console command, 51 console escape sequence, 46 accessing ILOM command line, 39 adapters for serial cables, 26 DB-9 TTY connector, 6 address, IP, 3 DHCP configuration, 38 addresses, web, See web sites...
  • Page 80: Contents

    #., 51 racks, compatible, 9 system initialization, normal, 47 removing server from rack, 21 system reset, 50 reset resetting the system with uadmin, 50 RJ-45 cable, 5 terms SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...
  • Page 81 slide rail assembly, 7 TTYA serial port, 6 uadmin command, 50 Index...
  • Page 82 SPARC Enterprise T5440 Server Installation and Setup Guide • July 2009...

Table of Contents