Overcurrent Protection Requirements; Assembling And Installing The Dc Input Power Cables - Sun Oracle SPARC T5120 Installation Manual

Hide thumbs Also See for SPARC T5120:
Table of Contents

Advertisement

Related Information
"Overcurrent Protection Requirements" on page 89

Overcurrent Protection Requirements

Overcurrent protection devices must be provided as part of each equipment rack.
Circuit breakers must be located between the DC power source and the server. Use
one 20 A fast-trip double-pole DC-rated circuit breaker for each power supply
unit.
Note – Overcurrent protection devices must meet applicable national and local
electrical safety codes and be approved for the intended application.
Related Information
"Assembling and Installing the DC Input Power Cables" on page 89
Assembling and Installing the DC Input
Power Cables
The following procedure describes how to assemble the DC input power cables for
the Sun SPARC Enterprise T5120 server.
Assemble one cable for each DC power supply in your server.
Assembling and Installing DC Power Cables for the Sun SPARC Enterprise T5120 Server
89

Advertisement

Table of Contents
loading
Need help?

Need help?

Do you have a question about the SPARC T5120 and is the answer not in the manual?

This manual is also suitable for:

T5220

Table of Contents