Optional T1000 2-Post Rack Fixed Installation Kit - 92801 - Toshiba t1000 Installation And Operation Manual

Single phase - 6 kva
Hide thumbs Also See for t1000:
Table of Contents

Advertisement

E.3 Optional T1000 2-Post Rack Fixed Installation Kit - 92801
T1000 Series UPS 2-Post Rack Fixed Kit Installation Instructions - 94035-000
1. Rackmount Fixed Installation - 2-Post
Use the 2-Post Fixed Rackmount Kit 92801 (1 kit per module) to mount a T1000 module in a 2-Post 19 inch
rack.
2. Contents - Fixed 2-Post Rack Installation Kit (92801)
1 ea.:
T1000 2-Post Rack Fixed Installation Kit Instructions - 94035
4 ea.:
92756 - Bracket, Fixed Mounting, 2-Post, Black
16 ea.: Cage Nut, 1/4"-20
16 ea.: Hex bolt, 1/4"-20 x 5/8"
16 ea.: Nut, Spin Lock, 1/4"-20 G5
12 ea.: Screw, PHP (Pan Head Phillips) 10-32 x 1/2" St Box
4 ea.:
Screw, PHP 8-32 x 1/4" St Zi
3. Prepare the 2-Post Rack (for rack rails with square holes)
1. Each 2-Post Fixed Mounting Bracket has 6 rack mounting holes. Place the bracket over the Rack Rail
at the lowest desired elevation for the system modules. Ensure all 6 bracket holes align with rack rail
holes.
2. Clip one cage nut (Cage Nut, 1/4"-20) at the top hole location on the rack rail, then clip cage nuts on the
rack rail in the 2nd, 5th, and 6th hole position on the rack rail.
NOTE: Ensure all bracket slots align with the rack rail mounting holes to establish the bottom unit eleva-
tion.
NOTE: If installing more than one T1000 module, begin with the lowest module first.
3. Repeat step 2 for the other three mounting bracket locations for the bottom module.
4. If more than one module is being installed for the T1000 system, install the next set of cage nuts from
the other module's 4-Post Slide Kit three (3) Rack Units (5 1/4") above the first set of cage nuts (Figure
5). Repeat steps 2-3.
5. Repeat steps 2-4 until cage nuts for all the modules in the system have been clipped on the 2-Post rack.
4. Install the 2-Post Rack Fixed Brackets
1. Bolt the 2-Post Fixed Bracket assembly to the 2-Post Rack using
four (4) 1/4"-20 x 5/8" bolts for each bracket. (Figure 1)
2. Hold one of the 2-Post Fixed Mounting Brackets, P/N 92756, against
the 2-Post rack rail at the level of the lowest module to be installed,
with the bracket folds to the inside of the 2-Post rack (Figure 1).
3. Each 2-Post Fixed Mounting bracket has 6 rack mounting holes. Slip
the hex bolt through the top (first) hole through the rack mounting
flange and secure it with the cage nut (square holes) or 1/4"-20 Spin
Lock Nut (round holes).
4. Slip a bolt through each of the brackets 2nd, 5th, and 6th holes and
secure each with the cage nut (square holes) or 1/4"-20 Spin Lock
Nut (round holes).
5.
Repeat Steps 2-4 for remaining three mounting brackets (Figure 2).
6. If more than one module is being installed for the T1000 system,
T1000 Series UPS Installation and Operation Manual – 91074-002
Inside of
Rack
1
1/4-20 x
5/8" Bolt
6
FIGURE. 1: 2-POST FIXED
BRACKET RACK MOUNTING
E-5