Toshiba t1000 Installation And Operation Manual page 107

Single phase - 6 kva
Hide thumbs Also See for t1000:
Table of Contents

Advertisement

6. If more than one module is being installed for the T1000 system, install the remaining mounting
bracket kits as described in steps 1-5.
5. Attach Rail Assemblies to 2-Post Adapter Brackets
1. Orient the Outer Channel Body of the Slide Assembly so the open side is facing inwards, and the
front is towards the rack front. Open and fully extend the slide inner channel from the outer channel.
NOTE: There are six (6) mounting holes available for use. The first two holes, Figure 5 - #1 and #2,
are accessible through openings in the Inner Channel when the Inner Channel is fully extended. The
Rear-most mounting hole (Figure 5 - #6) may be blocked by the 2-Post mounting bracket.
2. Bolt the Outer Channel Body (370ez-27-11), Figure 1-(3) to the Slide Mount Brackets. (4 places)
(See Figure 5) Recommend using holes #1, #2, #4, and #5 in Figure 5.
3. Insert the screws through the Outer Channel Body and 2-Post Slide Bracket (Figure 6).
4. Secure the four FHP 8-32 x 3/8 in. screws with the 8-32 serrated head nuts from 90400 kit. The nuts
screw on from the outside of the 2-Post Slide Bracket. (Figure 6)
5. Repeat steps 1-4 for the second slide assembly.
#1
#2
Intermediate
Channel
FIGURE 5: SLIDE OUTER CHANNEL MOUNTING HOLE LOCATIONS
FHP 8-32 x 3/8"
Nut 8-32 Serrated Head
FIGURE 6: ATTACH OUTER CHANNEL TO 2-POST SLIDE BRACKET (2 PER MODULE)
6. Repeat steps 1-5 for each module to be installed. (See Figure 7)
T1000 Series UPS Installation and Operation Manual – 91074-002
OUTER CHANNEL BODY
#3
(Back View)
Six (6) ea. 0.177 Thru Hole, Countersunk 0.332 x 100° Farside, typ.
Use FHP 8-32 x 3/8" to mount on slide brackets.
Insert Outer Channel Fasteners Through Outer Channel Body
OUTER CHANNEL
1/4-20 x
5/8" Bolt
2-POST RACK
#4
1/4-20 x
5/8" Bolt
#5
#6
Rear-most Outer
Channel mounting
hole may be blocked
by Slide Bracket.