Toshiba t1000 Installation And Operation Manual page 52

Single phase - 6 kva
Hide thumbs Also See for t1000:
Table of Contents

Advertisement

Remote Stop
The Remote Stop is triggered by an external NO (Normally Open) dry contact switch. Power to the
Remote Stop switch is about 10Vdc, and less than 20mA.
When the Remote Stop switch is closed, the UPS transfers from Normal/Backup to Bypass after a 1 – 2
sec. detection delay. (See the diagram below)
When the closed Remote Stop switch is opened, the UPS transfers from Bypass back to it's initial state
(Normal/Backup) after a 1 – 2 sec. detection delay.
If the UPS is in bypass when the Remote Stop is closed, no action is taken.
Detection Delay
Detection Delay
Closed
1-2 Sec.
1-2 Sec.
Remote Status
Open
Switch
UPS Mode
Normal / Backup Mode
Bypass Mode
FIGURE 14-2: REMOTE STATUS SHUTDOWN TIMING