5. Installation Precautions

1.
Observe the following environmental restrictions:
Install the unit in a well-ventilated location.
Install the unit where the ambient temperature is within the range specified in Appendix A -
"Specifications".
DO NOT install the UPS in areas that are subject to high humidity.
DO NOT install the UPS in areas that allow exposure to direct sunlight.
DO NOT install the UPS in areas that allow exposure to high levels of airborne dust, metal
particles, or flammable gases.
DO NOT install the UPS in areas near sources of electrical noise. Ensuring a proper earth ground
will reduce the effects of electrical noise and will reduce the potential for electrical shock.
DO NOT install the UPS in areas that would allow fluids or any foreign object to get inside the
UPS.
2.
Install the unit in a stable, level and upright position that is free of excessive vibration.
3.
Follow the instructions on the unpacking label affixed to the exterior of the UPS.
4.
Tower Unit with Caster Kit Option Only: Once the installation is complete, screw down the UPS
leveling feet located next to the front and back casters, until the unit is no longer resting on the
casters.
5.
The UPS generates and can radiate radio-frequency energy during operation. Although RFI noise
filters are installed inside of the unit, there is no guarantee that the UPS will not influence some
sensitive devices that are operating near by. If such interference is experienced, the UPS should be
installed farther away from the affected equipment and/or powered from a different source than that
of the affected equipment.
6.
It is the responsibility of the installer of this equipment to provide a suitable disconnect for the Control
Panel supplying power to this equipment.
This disconnect must:
Be suitable for the Voltage and Full Load Ampere Rating of all downstream equipment supplied by
the Panel;
The supply disconnecting device shall be one of the following types:
Switch-disconnect, with or without fuses, in accordance with IEC 60947-3, utilization category
AC-23B or DC-23B
As above, except one that has an auxiliary contact that in all cases causes switching devices
to break the load circuit before the opening of the main contacts of the disconnect.
A circuit breaker suitable as an isolation device per IEC 60947-2
Any other switching device in accordance with an IEC product standard that also meets the
isolation requirements of IEC 60947-1 and is appropriate for on-load switching of motors or
other inductive loads;
Be approved for use as a disconnect for the country in which this equipment is installed.
Be provided with a Lock Out Tag Out capability in the Off (Down) position.