Appendix A: T1000 Specifications - Toshiba t1000 Installation And Operation Manual

Single phase - 6 kva
Hide thumbs Also See for t1000:
Table of Contents

Advertisement

Appendix A: T1000 Specifications

NOTE: Except for size, weight, and Part Number, the Rackmount and Tower specifications are the same.
Parameter
GENERAL
Model No.
Power Module
Capacity Output
Topology
INPUT
Voltage (V)
Current (Nominal) (A)
Current (Max) @ 208 V (A)
Current (Max) @ 240 V (A)
Current (Min.) No-Load @ 240 V (A)
Current, Peak Inrush (A)
Current Limit (%)
Current THD (%)
Frequency (Hz) [and range]
Input Power Factor (PF) @ full load
Startup Delay (sec)
Ground leakage (max.) (mA)
Internal AC Input Breaker Rating
Surge Protection (kA or Category)
BYPASS
Voltage (V) (selectable)
Bypass Overload @ 125% Load (min)
Bypass Overload @ 1000% Load
Bypass Disable
Automatic Retransfer
(Max load % for Retransfer)
Max. Automatic Retransfer Attempts
Online Transfer Time – Inverter to By-
pass and Bypass to Inverter
T1000 Series UPS Installation and Operation Manual – 91074-002
T1000 SPECIFICATIONS - POWER MODULE
Rackmount
T1P0A6000GXGR3
T1P0A6000GXGR3L1
True Online, Double conversion, IGBT Power Factor Correction Input
Single Phase - 208/240 Vin +10% to -15% (L to L)*
(Adjustable to +10/-10%, or +15/-20%; set on front panel)
(*NOTE: Down to Vin -30% @ 70% Load)
Default: 0 sec (Range: 0 – 800 sec in 1 sec increments)
Set by display panel : +10/-15% of nominal (default);
NOTE: The Display software cannot make floating point (decimal) calculations. There
may be differences between the nominal and calculated BYPOV and BYPUV.
Example: BYPOV set to 115%, at 208V that should be 239.2V. The decimal value
.2 will be truncated (cut off) and the value 239V will be sent to the control board.
This will be read back to the display as 114% (114.9% truncates to 114%).
Automatic (when Input and Output Voltage/Frequency are set to differ-
4 ms (1/4 cycle) at <105% Max Load
Value
T1P0A6000GXG
T1P0A6000GXGL1
6 kVA
25 A @ 240 V (30 A @ 208 V)
32 A
25 A (32 A @ 85% of 240 V)
8 A (Typical)
20 A Peak (Typical)
125%
< 5%
45-65 Hz auto sensing ± 3 Hz
Greater than 0.97
5 mA (UPS only)
50 A, 240 V
MOV 250 Joules on Input
+10/-10% of nominal
+15/-20% of nominal
10 min.
1 cycle
ent values)
2
Less than 4 ms