T640 Dc Power Specifications And Requirements; T640 Dc Power System Electrical Specifications; Table 36: T640 Power System Electrical Specifications - Juniper T640 Hardware Manual

Core router
Hide thumbs Also See for T640:
Table of Contents

Advertisement

T640 DC Power Specifications and Requirements

T640 DC Power System Electrical Specifications

Related
Documentation
Copyright © 2010, Juniper Networks, Inc.
CAUTION: To comply with intrabuilding lightning and surge requirements,
intrabuilding wiring must be shielded, and the shield for the wiring must be
grounded at both ends.
WARNING: The intrabuilding port(s) of the equipment or subassembly is
suitable for connection to intrabuilding or unexposed wiring or cabling only.
The intrabuilding port(s) of the equipment or subassembly MUST NOT be
metallically connected to interfaces that connect to the OSP or its wiring.
These interfaces are designed for use as intrabuilding interfaces only (Type
2 or Type 4 ports as described in GR-1089-CORE, Issue 4) and require isolation
from the exposed OSP cabling. The addition of primary protectors is not
sufficient protection in order to connect these interfaces metallically to OSP
wiring.
T640 DC Power System Electrical Specifications on page 347
T640 DC Power Supply Electrical Specifications on page 348
T640 DC Power System Requirements on page 350
T640 DC Power Cable Specifications on page 352
T640 DC Power Distribution on page 353
Table 36 on page 347 lists the power system electrical specifications.

Table 36: T640 Power System Electrical Specifications

Item
DC input voltage
DC system current rating
T640 Power System Description on page 49
T640 DC Power Supply Electrical Specifications on page 348
Appendix D: T640 Power Guidelines, Requirements, and Specifications
Specification
Operating range: –40.0 to –72.0 VDC
NOTE: If the input voltage from the DC power
source drops below –37.5 to –39.5 VDC, the
router automatically shuts down. During
automatic shutdown, the circuit remains active.
When the input voltage returns to –43.0 to
–44.0 VDC, the router automatically starts up
again and the system returns to normal
operation within 30 minutes. No operator
intervention is required.
152 A @ –48 VDC (nominal) (7296 W)