Dc Supply And Ground Conductor Requirements - Oracle Sun SPARC Enterprise T5140 Installation Manual

Table of Contents

Advertisement

Related Information
"DC Supply and Ground Conductor Requirements" on page 94
DC Supply and Ground Conductor
Requirements
The server ground conductor must meet the following requirements:
Suitable conductor material: Use copper conductors only
Power supply connections through the input connector: 8 AWG (between the
server and the source). There are three conductors:
System ground conductor: 8 AWG (to be connected to the chassis)
Cable insulation rating: Minimum of 75˚C (167˚F), low smoke fume (LSF), flame
retardant
Provide the mating connector, Wago Part Number 51204745 for proper connection
to the DC connectors supplied with the server. This connection requires a 4mm
flat-blade screwdriver to insert wires into the connector body.
Branch circuit cable insulation color: According to applicable National Electrical
Codes
Grounding cable insulation color: Green/yellow
DC power source must meet TNV-2 requirements as defined by UL 60950-1 and
IEC 60950-1
Note – Depending on the DC power source, the -48V or -60V (negative terminal)
might be marked with a minus (-) symbol. The -48V or -60V Return (positive
terminal) might be marked with a positive (+) symbol.
When attaching DC cables, keep the following caution in mind:
Caution – You must restrict the connection of the server to the DC power source to
minimize the possibility that transient energy will appear on the main input to the
equipment. The DC battery power source must be in the same premises as the server.
The server cannot be in one building with the power source in another building.
94
Sun SPARC Enterprise T5140 and T5240 Servers Installation Guide • December 2010
-48V or -60V (negative terminal)
Chassis ground connection
-48V or -60V Return (positive terminal)