GE Reason Switches
10
Insulation, EMI and Environmental Tests
10.1
Insulation Tests
Description
Insulation Class
10.2
Type Tests
Test
IEC 61000-4-2
IEC 61000-4-3
IEC 61000-4-4
IEC 61000-4-5
IEC 61000-4-6
IEC 61000-4-8
IEC 61000-4-11
IEC 61000-4-29
IEC 61000-4-17
IEC 61000-4-18
Gradual Startup
CISPR11:2009
IEC 60068-2-1
IEC 60068-2-2
IEC 60068-2-30
IEC 60255-21-1
IEC 60255-21-2
REASON SWITCHES-TM-EN-3
Description
Electrostatic discharge immunity
Radiated RFI
Electrical fast transient
Surge immunity
Immunity to conducted disturbances induced
by radio-frequency fields
Magnetic Field
Voltage dips, short interruptions and voltage
variations
Ripple on DC input power port immunity test
Damped Oscillatory
Radiated emission
Cold temperature
Dry heat temperature
Damp heat temperature, cyclic (12 + 12 h
cycle)
Mechanic vibration
Mechanic shock and bump
Chapter 11 – Technical Specifications
Value
Class I
Test Levels
6 kV contact / 8 KV air
10 V/m
2 kV @5 kHz
Differential mode: 1 kV
Common mode: 2 kV
10 V
30 A/m continuous – 300 A/m @ 1 s
AC and DC voltage dips
Test level: 0% residual voltage
Duration time AC: 1 cycle
DC: 16.6 ms
Test level: 40% residual voltage
Duration time AC: 12 cycles
DC: 200 ms
Test level: 70% residual voltage
Duration time AC: 30 cycles
DC: 500 ms
AC and DC voltage interruptions
Test level: 0% residual voltage
Duration time AC: 300 cycles
DC:5s
Test level: 1 % of rated DC value
Test frequency: 120 Hz, sinusoidal
waveform.
Voltage oscillation frequency: 1 MHz
Differential mode: 1 kV peak voltage;
Common mode 2 kV peak voltage
Shut-down ramp: 60 s
Power off: 5 m Start-up ramp: 60 s
30 to 230 MHz – 50 dB (μV/m) quasi
peak at 3 m 230 to 1,000 MHz – 57 dB
(μV/m) quasi peak at 3 m
-40 °C, 16 Hours
+85 °C, 16 Hours
95% (non-condensing), 55 °C
2 g @ (10 - 150) Hz
15 g @ 11 mS
301