GE T1000 Technical Manual page 35

Reason, industrial managed ethernet switches
Table of Contents

Advertisement

Chapter 2 – Safety Information
REASON SWITCHES-TM-EN-3
Terminals exposed during installation, commissioning
and maintenance may present a hazardous voltage
unless the equipment is electrically isolated.
Tighten M3 clamping screws of heavy duty terminal block
connectors
to
a
Tighten captive screws of header-type (Euro) terminal blocks
to 0.5 Nm minimum and 0.6 Nm maximum.
Always use insulated crimp terminations for voltage and
current connections.
Always use the correct crimp terminal and tool according to
the wire size.
In order to maintain the equipment's requirements for
protection
against
connected to Reason Switches shall have protective class
equal or superior to Class 1.
Watchdog (self-monitoring) contacts are provided to indicate
the health of the device on some products. We strongly
recommend that you hard wire these contacts into the
substation's automation system, for alarm purposes.
Ground the equipment with the supplied PCT (Protective
Conductor Terminal).
Do not remove the PCT
GE Reason Switches
nominal
torque
of
electric
shock,
other
1.0
Nm.
devices
35

Hide quick links:

Advertisement

Table of Contents
loading

This manual is also suitable for:

S2020S2024g

Table of Contents