2. Confirm that you have completed the installation of the server in its rack.
See the instructions in
on page
19.
3. Connect a terminal or a terminal emulator (PC or workstation) to the service
processor serial management port.
Configure the terminal or terminal emulator with these settings:
9600 baud
8 bits
No parity
1 Stop bit
No handshake
A null modem configuration is needed, meaning the transmit and receive signals
are reversed (crossed over) for DTE to DTE communications. You can use the
supplied RJ-45 crossover adapters with a standard RJ-45 cable to achieve the null
modem configuration.
Note – When you power on the server for the first time and you do not have a
terminal or terminal emulator (PC or workstation) connected to the service processor
serial management port, you will not see system messages.
(Optional) Connect an Ethernet cable between the server's NET MGT port and the
network to which future connections to the SP and host will be made.
4. After the initial configuration of the system using the SP SER MGT port,
communication with the SP and host is usually performed through this Ethernet
interface.
Connect an Ethernet cable between one of the server's NET ports and the network
to which the server will communicate.
"Installing the SPARC Enterprise T5120 and T5220 Servers"
Powering On the System