About Fan Trays; Remove A Fan Tray (Hot-Swap) - Fujitsu SPARC Enterprise T5440 Service Manual

Fujitsu server user manual
Hide thumbs Also See for SPARC Enterprise T5440:
Table of Contents

Advertisement

"Fan Tray Fault LED" on page 89

About Fan Trays

Four fan trays are located toward the front of the server, arranged in two N+1
redundant pairs. Each fan tray contains a fan mounted in an integrated,
hot-swappable CRU. If a fan tray fails, replace it as soon as possible to maintain
server availability.
Caution – Hazardous moving parts. Unless the power to the server is completely
shut down, the only service permitted in the fan compartment is the replacement of
the fan trays by trained personnel.
Related Information
"Identifying Server Components" on page 1
"Managing Faults" on page 11
"Powering Off the System" on page 67
"Hot-Pluggable and Hot-Swappable Devices" on page 75
"Fan Tray Device Identifiers" on page 88
"Fan Tray Fault LED" on page 89
"Server Components" on page 177

▼ Remove a Fan Tray (Hot-Swap)

Before you begin, complete these tasks:
Read the section,
Perform the task,
Perform the task,
Measures" on page
Do the following :
1. Identify the fan tray to be removed.
See
"Fan Tray Device Identifiers" on page 88
page
89.
2. Press the fan tray latches toward the center of the fan tray and pull the fan tray
up and out of the system.
"Safety Information" on page
"Extend the Server to the Maintenance Position" on page
"Perform Electrostatic Discharge – Antistatic Prevention
73.
63.
and
"Fan Tray Fault LED" on
Servicing Customer-Replaceable Units
70.
85