20 Troubleshooting
Code
Name
SEr
Speed Search Retries Exceeded
STPo
Motor Step-Out Detected
SvE
Zero Servo Fault
TiM
Keypad Time Not Set
UL3
Undertorque Detection 1
UL4
Undertorque Detection 2
UL5
Mechanical Weakening Detection 2
Uv1
DC Bus Undervoltage
Uv2
Control Power Undervoltage
Uv3
Soft Charge Answerback Fault
◆
Minor Faults/Alarms
This section gives information about the causes and possible solutions when a minor fault or alarm occurs. Use the
information in this table to remove the cause of the minor fault or alarm.
Code
Name
AEr
Station Address Setting Error
bAT
Keypad Battery Low Voltage
bb
Baseblock
bCE
Bluetooth Communication Error
boL
Braking Transistor Overload
bUS
Option Communication Error
CALL
Serial Comm Transmission Error
90
Causes
The speed search-related parameters are set
incorrectly.
The motor code is set incorrectly for PM Control
Methods.
The value set in the torque limit is too small.
There is a battery in the keypad, but the date and time
are not set.
A fault occurred on the machine.
Example: There is a broken pulley belt.
A fault occurred on the machine.
Example: There is a broken pulley belt.
The drive detected undertorque as specified by the
conditions for mechanical weakening detection set in
L6-08 [Mechanical Fatigue Detect Select].
There is a phase loss in the drive input power.
The value set in L2-02 [Power Loss Ride Through
Time] increased and the momentary power loss
recovery unit is not connected to the drive.
The relay or contactor on the soft-charge bypass relay
is damaged.
Causes
The node address for the communication option is not
in the permitted setting range.
The keypad battery voltage is low.
An external baseblock command was entered through
one of the MFDI terminals Sx, and the drive output
stopped as shown by an external baseblock command.
The smartphone or tablet with DriveWizard Mobile
installed is too far from the keypad.
Radio waves from a different device are causing
interference with communications between the
smartphone or tablet and keypad.
The duty cycle of the braking transistor is high (the
regeneration power or repetition frequency is high).
The communications cable wiring is incorrect.
The communications cable wiring is incorrect.
There is a short circuit in the communications cable
or the communications cable is not connected.
A programming error occurred on the controller side.
YASKAWA TOEPC71061782C GA800 Drive Installation & Primary Operation
Possible Solutions
• Decrease b3-10 [Speed Estimation Detection Gain].
• Increase b3-17 [Speed Est Retry Current Level].
• Increase b3-18 [Speed Est Retry Detection Time].
• Do Auto-Tuning again.
• Set E5-01 [PM Motor Code Selection] correctly as specified by
the motor.
• For specialized motors, refer to the motor test report and set E5-
xx correctly.
Adjust torque limit-related parameters L7-01 to L7-04.
Use the keypad to set the date and time.
Examine the machine and remove the cause of the fault.
Examine the machine and remove the cause of the fault.
Examine the machine for deterioration.
Correct errors with the wiring for main circuit drive input power.
Connect the momentary power loss recovery unit to the drive.
• Re-energize the drive.
• If the fault stays, replace the control board or the drive.
• Check monitor U4-06 [PreChargeRelayMainte] shows the
performance life of the soft-charge bypass relay. If U4-06 is
more than 90%, replace the board or the drive. For information
about replacing the control board, contact Yaskawa or your
nearest sales representative.
Possible Solutions
• For CC-Link communication, set F6-10 [CC-Link Node Address]
correctly.
• For MECHATROLINK communication, set F6-20
[MECHATROLINK Station Address] correctly.
• For CANopen communication, set F6-35 [CANopen Node ID
Selection] correctly.
Replace the keypad battery.
Examine the external sequence and timing of the baseblock
command input.
Use the smartphone or tablet 10 m (32.8 ft.) or nearer to the keypad.
Note:
bCE can occur when the smartphone or tablet is 10 m (32.8 ft)
or nearer to the keypad depending on the specifications of the
smartphone or tablet.
Make sure that no device around the keypad uses the same radio
bandwidth (2400 MHz to 2480 MHz), and prevent radio
interference.
• Install a braking unit (CDBR series).
• Install a regenerative converter.
• Increase the deceleration time.
Correct wiring errors.
Correct wiring errors.
• Repair the short-circuited or disconnected portion of the cable.
• Replace the defective communications cable.
Examine communications at start-up and correct programming
errors.