10 Drive Start-Up
A - Drive front
B - LED status ring board
A - Drive front
B - LED status ring board
2.
Refer to the following figure and wire the control circuit.
WARNING
or too tight can cause incorrect operation and damage to the drive. Incorrect connections can also cause death or serious
injury from fire.
Note:
• Use shielded, twisted-pair wires and ground the shield to the ground terminal of the drive. Incorrect equipment grounding can
cause drive or equipment malfunction from electrical interference.
• Do not use control circuit wiring that is longer than 50 m (164 ft) to supply the analog frequency reference from a remote source.
If the control circuit wiring is too long, it can cause unsatisfactory system performance.
46
Figure 10.6 Remove the LED Status Ring Board
Figure 10.7 Remove the LED Status Ring Board
Fire Hazard. Tighten all terminal screws to the correct tightening torque. Connections that are too loose
C - Temporary placement holes
C - Temporary placement holes
YASKAWA TOEPC71061782C GA800 Drive Installation & Primary Operation