Fujitsu SPARC Enterprise T5220 Service Manual page 154

Fujitsu server user manual
Hide thumbs Also See for SPARC Enterprise T5220:
Table of Contents

Advertisement

FIGURE:
2. Apply firm pressure to fully seat the fan module.
3. Verify that the Fan Fault LED on the replaced fan module is off.
4. Close the top cover door.
5. Verify that the system Fan Fault LED, Service Required LEDs, and the
individual fan module Fault LED are off.
6. Run the ILOM show faulty command to verify that the fan fault has been
cleared.
See
show faulty command.
Related Information
"Extend the Server to the Maintenance Position" on page 63
"Faults Displayed by show faulty" on page 29
128
SPARC Enterprise T5120 and T5220 Servers Service Manual • July 2009
Installing a Fan Module
"Detecting Faults With ILOM" on page 22
for more information on using the

Advertisement

Table of Contents
loading

This manual is also suitable for:

Sparc enterprise t5120

Table of Contents