Minimum Gas Pressure Switch; Final Checks (With Burner Operating) - Riello DB 4 SM C03 A0 TC FS1 FB T150 Installation, Use And Maintenance Instructions

Industrial gas burners
Hide thumbs Also See for DB 4 SM C03 A0 TC FS1 FB T150:
Table of Contents

Advertisement

Available languages

Available languages

6.9.3

Minimum gas pressure switch

Adjust the minimum gas pressure switch after performing all the
other burner adjustments with the pressure switch set to the start
of the scale (Fig. 27).
With the burner operating at maximum output, increase adjust-
ment pressure by slowly turning the relative knob clockwise until
the burner locks out. Then turn the knob anticlockwise by 0.2 (2
mbar) and repeat burner start-up to ensure it is operating regular-
ly. If the burner locks out again, turn the knob again anticlockwise
by 0.1 kPa (1 mbar).
1 kPa = 10 mbar
WARNING
6.10

Final checks (with burner operating)

➤ Open the thermostat/pressure switch TL
➤ Open the thermostat/pressure switch TS
➤ Turn the gas maximum pressure switch knob to the mini-
mum end of scale position
➤ Turn the air pressure switch to the maximum end of scale
position
➤ Turn off the burner and cut off the power
➤ Disconnect the minimum gas pressure switch connector
➤ Disconnect the QRI cell wire
Make sure that the mechanical locking systems
on the various adjustment devices are fully tight-
ened.
WARNING
20117017
Start-up, calibration and operation of the burner
The burner must stop
The burner must stop in lockout
The burner must not start
The burner must stop in lockout due to ignition failure
26
GB
D3855
Fig. 27
Tab. K

Advertisement

Chapters

Table of Contents
loading

This manual is also suitable for:

Db 6 sm c03 a0 tc fs1 fb t1502011659720119591

Table of Contents