Expanded operating temperature

Table 26. Expanded operating temperature specifications
Expanded operating temperature
Continuous operation
≤ 1% of annual operating hours
NOTE:
When operating in the expanded temperature range, system performance may be impacted.
NOTE:
When operating in the expanded temperature range, ambient temperature warnings may be reported in the System Event
Log.

Expanded operating temperature restrictions

Do not perform a cold startup below 5°C.
The operating temperature specified is for a maximum altitude of 3048 m (10,000 ft).
Two non-redundant power supply units are required.
Two non-redundant system fans are required.
Non-Dell qualified peripheral cards and/or peripheral cards greater than 25 W are not supported.
GPU is not supported.
Tape backup unit is not supported.

Particulate and gaseous contamination specifications

The following table defines the limitations that help avoid any equipment damage or failure from particulate and gaseous contamination. If
the levels of particulate or gaseous pollution exceed the specified limitations and result in equipment damage or failure, you may need to
rectify the environmental conditions. Remediation of environmental conditions is the responsibility of the customer.
Table 27. Particulate contamination specifications
Particulate contamination
Air filtration
38
Dell EMC PowerEdge T440 Installation and Service Manual
Technical specifications
Specifications
5°C to 40°C at 5% to 85% RH with 29°C dew point.
NOTE:
Outside the standard operating temperature (10°C to
35°C), the system can operate continuously in temperatures as low
as 5°C and as high as 40°C.
For temperatures between 35°C to 40°C, de-rate maximum allowable
temperature by 1°C per 175 m above 950 m (1°F per 319 ft).
–5°C to 45°C at 5% to 90% RH with 29°C dew point.
NOTE:
Outside the standard operating temperature (10°C to
35°C), the system can operate down to –5°C or up to 45°C for a
maximum of 1% of its annual operating hours.
For temperatures between 40°C and 45°C, de-rate maximum allowable
temperature by 1°C per 125 m above 950 m (1°F per 228 ft).
Specifications
Data center air filtration as defined by ISO Class 8 per ISO 14644-1 with a
95% upper confidence limit.