Particulate and gaseous contamination specifications

The following table defines the limitations that help avoid any equipment damage or failure from
particulates and gaseous contamination. If the levels of particulates or gaseous pollution exceed the
specified limitations and result in equipment damage or failure, you may need to rectify the
environmental conditions. Re-mediation of environmental conditions is the responsibility of the
customer.
NOTE: This section defines the limits to help avoid IT equipment damage and/or failure from
particulates and gaseous contamination. If it is determined that levels of particulates or gaseous
pollution are beyond the limits specified below and are the reason for the damage and/or failures to
your equipment, it may be necessary for you to re-mediate the environmental conditions that are
causing the damage and/or failures. Re-mediation of environmental conditions will be the
responsibility of the customer.
Table 25. Particulate contamination specifications
Particulate contamination
Air Filtration
NOTE: Applies to data center environments only.
Air filtration requirements do not apply to IT
equipment designed to be used outside a data
center, in environments such as an office or factory
floor.
Conductive Dust
NOTE: Applies to data center and non-data center
environments.
Corrosive Dust
44
Temperature or Specification
Six consecutively executed shock pulses in
the positive and negative x, y, and z axes (one
pulse on each side of the system) of 71 G for
up to 2 ms.
3,048 m (10,000 ft)
12,000 m (39,370 ft).
Maximum temperature is reduced by 1
°C/300 m (1 °F/547 ft) above 950 m (3,117 ft).
Maximum temperature is reduced by 1 °C/175
m (1 °F/319 ft) above 950 m (3,117 ft).
Maximum temperature is reduced by 1 °C/125
m (1 °F/228 ft) above 950 m (3,117 ft).
Specifications
Data center air filtration as defined by ISO
Class 8 per ISO 14644-1 with a 95% upper
confidence limit.
NOTE: Air entering the data center must
have MERV11 or MERV13 filtration.
Air must be free of conductive dust, zinc
whiskers, or other conductive particles.
Air must be free of corrosive dust.