Incorrect Operating Input Voltage Values for the 1.6
GHz, 8-Disk Configuration
The table that describes input power requirements for the SPARC Enterprise T5240 server
configuration with 1.6 GHz CPUs and an 8-disk capable backplane states the wrong
operating input voltage value in two places. The following table describes the necessary
correction.
Location of Incorrect Values
Table for T5240 Server, 1.6 GHz CPU, 8-disk backplane
Operating input voltage range
Maximum operating input current
Note – The operating input voltage range for the DC input model is correct.
Note – The 200 to 240 VAC operating input voltage range is required only for servers
equipped with 16-disk capable backplanes. All other configurations support the 100 to 240
VAC operating voltage range.
SPARC Enterprise T5140 and T5240 Servers
Installation Guide
This manual includes descriptions using the cable management arm (CMA); however, the
SPARC Enterprise T5140 server doesn't support the cable management arm.
Verify Proper Seating of Preinstalled PCIe/XAUI
Cards
The server installation procedure should include instructions for verifying that any
preinstalled PCIe and/or XAUI cards and their risers have not worked loose during shipping.
This procedure should also include instructions for verifying that internal cables are properly
routed and that their connections are secure.
52
SPARC Enterprise T5140 and T5240 Servers Product Notes • November 2012
Incorrect Value
200 to 240 VAC
At 100 VAC: <n/a>
Correct Value
100 to 240 VAC
At 100 VAC: 14.0A