Fujitsu SPARC Enterprise T5140 Product Notes page 95

Sparc enterprise
Hide thumbs Also See for SPARC Enterprise T5140:
Table of Contents

Advertisement

Example of fault indication not being cleared:
sc> showfaults
Last POST Run: Mon May 31 05:57:59 2010
Post Status: Passed all devices
ID FRU
1 /SYS/PS0
sc>
sc> showenvironment (partial excerpt)
:
------------------------------------------------------------------------------
System Indicator Status:
/SYS/LOCATE
OFF
------------------------------------------------------------------------------
/SYS/PS_FAULT
ON
:
Workaround: None. The replacement PSU has no errors. Since this is just an issue of
display, perform the ILOM reset operation to recover. The ILOM reset operation has no
impact on the system.
ILOM reset operation example:
Log in to ILOM and execute the following command.
[Using ILOM command mode]
-> reset /SP
Are you sure you want to reset /SP (y/n)? y
[Using ALOM CMT compatible shell]
sc> resetsc
Are you sure you want to reset the SC [y/n]? y
Fujitsu 4Gbps Fibre Channel Card Is Falsely Recognized as
F20 Card (CR 6947945)
This issue is resolved by updating the system firmware to 7.2.10 or later.
Fault
SP detected fault: Fan fault at PS0 asserted
/SYS/SERVICE
ON
/SYS/TEMP_FAULT
OFF
/SYS/ACT
ON
/SYS/FAN_FAULT
OFF
Appendix A
Fixed Issues
85

Advertisement

Table of Contents
loading

This manual is also suitable for:

Sparc enterprise t5240

Table of Contents