Particulate And Gaseous Contamination Specifications - Dell EMC PowerEdge T340 Installation And Service Manual

Hide thumbs Also See for EMC PowerEdge T340:
Table of Contents

Advertisement

Tape backup unit is supported.

Particulate and gaseous contamination specifications

The following table defines the limitations that help avoid any damages to the IT equipment and/or, or both failure from particulate and
gaseous contamination. If the levels of particulate or gaseous pollution exceed the specified limitations and results in equipment damage or
failure, you must rectify the environmental conditions. Remediation of environmental conditions is the responsibility of the customer.
Table 30. Particulate contamination specifications
Particulate contamination
Air filtration
Conductive dust
Corrosive dust
Table 31. Gaseous contamination specifications
Gaseous contamination
Copper Coupon Corrosion
Silver Coupon Corrosion
NOTE:
Maximum corrosive contaminant levels measured at ≤50% relative humidity.
116
Technical specifications
Specifications
Data center air filtration as defined by ISO Class 8 per ISO 14644-1
with a 95% upper confidence limit.
NOTE:
This condition applies to data center
environments only. Air filtration requirements do not
apply to IT equipment designed to be used outside a
data center, in environments such as an office or factory
floor.
NOTE:
Air entering the data center must have MERV11
or MERV13 filtration.
Air must be free of conductive dust, zinc whiskers, or other
conductive particles.
NOTE:
This condition applies to data center and non-
data center environments.
Air must be free of corrosive dust.
Residual dust present in the air must have a deliquescent point
less than 60% relative humidity.
NOTE:
This condition applies to data center and non-
data center environments.
Specifications
<300 Å/month per Class G1 as defined by ANSI/ISA71.04-1985.
<200 Å/month as defined by AHSRAE TC9.9.

Advertisement

Table of Contents
loading

This manual is also suitable for:

E60sVh1jv

Table of Contents