Table 27. Operating temperature derating specifications
Operating temperature derating
Up to 35°C (95°F)
35–40°C (95–104°F)
40–45°C (104–113°F)

Standard operating temperature

Table 28. Standard operating temperature specifications
Standard operating temperature
Continuous operation (for altitude less than 950 m or 3117
ft)

Expanded operating temperature

Table 29. Expanded operating temperature specifications
Expanded operating temperature
Continuous operation
≤ 1% of annual operating hours
NOTE:
When operating in the expanded temperature range, the performance of the system may be impacted.
NOTE:
When operating in the expanded temperature range, ambient temperature warnings may be reported on the
System Event Log.
Expanded operating temperature restrictions
Do not perform a cold startup of the system below 5°C.
The operating temperature specified is for a maximum altitude of 950 m for Fresh Air cooling.
Two redundant power supply units are required.
Cooling redundancy is not supported due to single fan only in system.
Support up to 80 W processor.
One system fan is required.
Non-Dell qualified peripheral cards and/or peripheral cards greater than 25 W are not supported.
GPU is not supported.
Specifications
Maximum temperature is reduced by 1°C/300 m (1°F/547 ft), above 950 m
(3,117 ft).
Maximum temperature is reduced by 1°C/175 m (1°F/319 ft), above 950 m
(3,117 ft).
Maximum temperature is reduced by 1°C/125 m (1°F/228 ft), above 950 m
(3,117 ft).
Specifications
10–35°C (50–95°F) with no direct sunlight on the equipment.
Specifications
5°C–40°C at 5% to 85% RH with 29°C dew point.
NOTE:
Outside the standard operating temperature
(10°C–35°C), the system can operate continuously in
temperatures as low as 5°C and as high as 40°C.
For temperatures 35°C– 40°C, derate maximum allowable
temperature by 1°C per 175 m (1°F per 319 ft) above 950 m
(3,1171 ft).
-5°C–45°C at 5% to 90% RH with 29°C dew point.
NOTE:
Outside the standard operating temperature
(10°C–35°C), the system can operate down to -5°C or
up to 45°C for a maximum of 1% of its annual operating
hours.
For temperatures 40°C– 45°C, derate maximum allowable
temperature by 1°C per 125 m (1°F per 228 ft) above 950 m (3.117
ft).
Technical specifications