5
Preparation for start up
5.1
Combustion head setting
Loosen the screw 1) and turn the graduated sector 2) according dia-
grams Fig. 19.
The system allows an optimal setting even at a minimum firing rate.
Combustion head opening can be varied by moving the lever onto
holes from 0 to 6, Fig. 18.
The choice of the hole (0 - 6) to be used is decided on the basis of di-
agram (Fig. 19) against the required maximum output. Setting is pre-
arranged in the plant for the maximum power (hole 6).
When dealing with boilers featuring a strong back pressure, if air deliv-
ery is insufficient even with the damper fully open, you can use a differ-
ent setting to that illustrated in diagram (Fig. 19) - do this by moving
the lever onto the next highest hole numerically speaking, thus increas-
ing the combustion head's opening and hence air delivery.
DB 4 SM
N° Hole
3
2
1
0
1600
DB 6 SM
N° Hole
3
2
1
0
4000