Quality Of Heating Water; Heating System Safety Valve Drain; Filling The Heating System - Ochsner AIR FALCON 212 C11A T200 Design And Installation Manual

High efficiency air/water heat pumps
Table of Contents

Advertisement

Appliance installation
9.3.2

Quality of heating water

Use the correct fill water that is suitable for the components
of your heating system. We recommend fill water prepared
according to Guideline VDI 2035-2.
A high pH value and low electrical conductivity in the fill
water will reduce to a minimum the risk of corrosion to iron
and copper materials, as long as there is also a low oxygen
content. This will also minimise scaling (calcification).
Fill water characteristics
pH value at 25°C
Electrical conductivity at 25°C
Oxygen content
Chloride
Water hardness
Material damage
Unsuitable fill water can damage your system due
to scaling and corrosion.
»
If necessary, ensure that the fill water is pro-
fessionally softened and desalinated.
9.3.3

Heating system safety valve drain

Note
The indoor unit has an internal safety valve (DHW,
heating).
»
Observe national and regional regulations re-
garding the design of the drain and prescribed
regular operational tests.
If the valve is activated, the water is drained off via a hose
on the rear of the indoor unit.
»
Size the safety valve drain so that the water can drain
freely via an open and readily visible waste water
drain.
»
Install the hose with a consistent fall to the drain.
Avoid kinking the hose.
»
Secure the drain hose to prevent movement when
water is running out.
WARNING: Burns
The water that escapes when it is triggered is hot
and can cause scalding on contact with skin.
»
Implement the safety valve drain in such a
manner that there can be no contact with the
water escaping from the machine.
PIA-982043-AIR FALCON-T200-in-EN | www.ochsner.com
8.5-10
< 100 μS/cm
< 0.05 mg/l
< 30 mg/l
< 3 °dH
1 Drain hose
2 Fixing
3 Drain
9.3.4

Filling the heating system

Note
To protect the potable water supply, a heating sys-
tem with an AIR FALCON C11B T201 must be filled
in accordance with the UK Water Supply (Water
Fittings) Regulations 1999, Section 8 G24.
»
Fill the heating system with suitable fill water using
the drain and fill valve.
1 Fill and drain stopcock
»
Vent the pipework.
Note
For easier filling, the 3-way switching module is
set to a position suitable for filling at the factory.
The cable from the 3-way switching module to the
controller has been disconnected at the factory.
»
After filling, plug the connector into the 3-way
switching module.
39