Machine-specific engineering and preparation
8.
Machine-specific engineering
and preparation
Material damage
Air pressure and air humidity will affect the opera-
tional reliability of the electrical components in the
heat pump system (dielectric strength).
»
Observe the maximum installation altitude of
the heat pump system.
Unit
AIR FALCON
m
212
8.1
Outdoor unit
8.1.1
Installation location
►
The outdoor unit must not be surrounded by walls/
objects on all four sides.
►
The outdoor unit must not be positioned immediately
adjacent to walls/objects on one, two or three sides.
20
Max. installation altitude (above
sea level)
2000
Material damage
The outdoor unit must be positioned so that the
air flow is not blocked by accumulation of snow
in winter.
»
Take into account the expected depth of snow
at the installation site and position the outdoor
unit at a sufficient height above the ground.
»
If necessary, construct a canopy above the
outdoor unit to protect it from any large accu-
mulation of snow.
»
Make sure that snow falling at the sides does
not damage the outdoor unit. If necessary
install a deflection plate to divert the snow.
When doing so, observe the machine-specific
minimum clearances.
►
When installing the outdoor unit, the expected wind
direction must be taken into account.
1 Wind direction
►
The outdoor unit should be positioned with the air
outlet side facing a wall, ensuring that minimum clear-
ances are observed; this protects the air outlet side
from direct exposure to winds.
www.ochsner.com | 00_200_202_08_01_002-EN