Ochsner AIR FALCON 212 C11A T200 Design And Installation Manual page 21

High efficiency air/water heat pumps
Table of Contents

Advertisement

Machine-specific engineering and preparation
Note
In areas with low outdoor temperatures, the air
outlet side must not be directly exposed to winds.
»
Position the outdoor unit adjacent to a wall,
ensuring that minimum clearances are ob-
served.
8.1.2
Minimum clearances
The outdoor unit may be installed adjacent to walls/
objects on one, two or three of its sides provided
that the air outlet side remains clear and the ma-
chine-specific minimum clearances are observed.
It is permissible to install the outdoor unit under a roof
if the unit is permanently surrounded by open space
on three sides and the machine-specific minimum
clearances are observed.
00_200_202_08_01_002-EN | www.ochsner.com
It is permissible to install the outdoor unit with both its
air outlet side and air inlet side facing walls/objects,
provided that the other two sides around the outdoor
unit are kept clear at all times and the machine-spe-
cific minimum clearances are observed.
Several outdoor units may be installed next to each
other, provided the machine-specific minimum clear-
ances are observed.
The mounting feet of the outdoor unit must be at least
80 mm clear of the surrounding terrain.
21