Indicator Codes For Non-Redundant Power Supply - Dell PowerEdge T430 Owner's Manual

Dell poweredge t430 tower server
Hide thumbs Also See for PowerEdge T430:
Table of Contents

Advertisement

Convention
Power Indicator
Pattern
E
Not lit

Indicator codes for non-redundant power supply

Press the self-diagnostic button to perform a quick health check on the non-redundant power supply of
the system.
Figure 9. Non-redundant AC power supply status indicator and self-diagnostic button
1.
self-diagnostic button
Diagnostic Indicator Pattern
Not lit
Green
24
Description
CAUTION: When correcting a power supply mismatch, replace
only the power supply with the flashing indicator. Swapping
the other power supply to make a matched pair can result in
an error condition and unexpected system shutdown. To
change from a High Output configuration to a Low Output
configuration or vice versa, you must power down the system.
CAUTION: AC power supplies support both 220 V and 110 V
input voltages with the exception of Titanium power supplies,
which support only 220 V. When two identical power supplies
receive different input voltages, they can output different
wattages, and trigger a mismatch.
CAUTION: If two power supplies are used, they must be of the
same type and have the same maximum output power.
CAUTION: Combining AC and DC power supplies is not
supported and triggers a mismatch.
Power is not connected.
2.
Description
Power is not connected or power supply is faulty.
A valid power source is connected to the power supply and