SECTION 5 - SYSTEM TEST MESSAGES
5.164 R-R O/R VALVE
System test prompt indicating that it is currently testing this circuit.
5.165 R-R OUTRIGGER LAMP ON
System test prompt to check that the ground Rear-Right Outrigger lamp is illuminated.
Step
Pretest Instructions
5.165.1
5.165.2
5.165.3
5.165.4
5.166 R-R OUTRIGGER VALVE OPEN CIRCUIT
The system test detected an open in the Rear-Right Outrigger valve circuit.
See 2.132 Rear-Right O/R Solenoid Open Circuit

5.167 R-R OUTRIGGER VALVE SHORT TO BATTERY

The system test detected a short to battery in the Rear-Right Outriggers valve circuit.
See 2.133 Rear-Right O/R Solenoid Short To Battery

5.168 R-R OUTRIGGER VALVE SHORT TO GROUND

The system test detected a short to ground in the Rear-Right Outriggers valve circuit.
See 2.134 Rear-Right O/R Solenoid Short To Ground

5.169 RUNNING

System test prompt indicating that it is currently running tests

5.170 START CL

ENGINE POWERED MACHINES ONLY
System test response indicating that the ground start switch has been closed when a different switch was expected. Make
sure the correct switch is being activated or check the switch wiring.
5-152
Test
Does this indicator illuminate
Yes
properly?
No
Do other indicators illuminate
Yes
instead?
No
Voltage at X030.7 = 12VDC? Yes
No
Voltage at X004.14 =
Yes
12VDC?
No
T350 T500J
Result
Corrective Action
Press ENTER on the analyzer to con-
tinue the system test
Go to step 5.165.2
Possible Causes: Check wiring
Go to step 5.165.3
Possible Causes: 4.1.27
Go to step 5.165.4
Possible Causes: Check wires Brn/
Wht 47-23, Brn/Wht 47-23-1, and
Black
Possible Causes: 4.1.10