Advanced confi guration
Cycles Per Hour (CPH) for Heat Stage 1: Select Cycles Per Hour for Heat Stage 1;
0 disables cycling and thermostat becomes an ON/OFF control
Menu
32
Default: 5 CPH
Recovery Rate for Heat: Set temperature for heat recovery rate; 0 disables ramp
recovery, uses step response
Menu
35
Default: 5°F/Hr, 3°C/Hr Options:
Recovery Rate for Cool: Set temperature for cool recovery rate; 0 disables ramp
recovery, uses step response
Menu
36
Default: 5°F/Hr, 3°C/Hr Options:
Output Minimum Off Time for Heat and Cool: Set the minimum "off time" for heat and
cool output
Menu
40
Default: 4 min.
Temp Source: Allows use of remote sensor option on R2500
Menu
42
Default: 0
Pairing Start: Allows pairing of T2500 Thermostat with the R2500 Receiver
Menu
43
Default: 0
Intermittent Fan Enable: If enabled, intermittent fan will cycle when there is no demand
Menu
45
Default: 0
Intermittent Fan On Time: Minutes the fan will be on when intermittent fan is enabled
Menu
46
Default: 5 min.
© COPYRIGHT 2010 PECO, INC. ALL RIGHTS RESERVED. P/N 70161 3220-2216 Rev 0
Options:
0 to 12 CPH
0-18°F/Hr, 0-10°C/Hr
0-18°F/Hr, 0-10°C/Hr
Options:
1-10 minutes
0= Temperature will be measured by T2500 internal sensor
1= Temperature will be measured by R2500 remote sensor
Options
0,1
0= OFF: Not pairing: Thermostat will not pair with the R2500
Receiver
1= ON: Pairing: Thermostat will attempt to pair with the
R2500 Receiver
Options
0,1
0= Disable
1= Enable
Options
0, 1
Options:
1-60 min.
16
Selection:_________
Selection:_________
Selection:_________
Selection:_________
Selection:_________
Selection:_________
Selection:_________
Selection:_________