Maintenance; Checking The Flame Detector; Periodic Checks - Riello DB 6 LM C10 TC FS1 A0 T150 Installation, Use And Maintenance Instruction

Oil industrial burner
Hide thumbs Also See for DB 6 LM C10 TC FS1 A0 T150:
Table of Contents

Advertisement

7

Maintenance

7.1

Checking the flame detector

UV cell
Minimum current for correct working is 70 μA.
If the value is lower, it could be due to:
exhausted photocell;
low current (lower than 187 V);
bad regulation of the burner.
In order to measure the current, use a microamme-
ter of 100 A c.c., connected in series to the photocell, as in the scheme, with a capacitor of 100 F - 1V c.c. at the same level of
the instrument.
7.2

Periodic checks

We recommend carrying out the following checks:
LIST OF MONTHLY CHECKS
1 Inspect the flame detection device and check it is undamaged and clean.
2 Check the ignition device and clean if necessary.
3 Check the right pressure levels for fuel and air.
4 Check the correct movement and setting of the air damper and relative lifting assemblies.
5 Check the start up sequence and the safety interlocks, by simulating the relative anomaly situation.
LIST OF YEARLY CHECKS
1 Check the fuel blocking valves are still well sealed.
2 Check the settings on the pressure switches.
3 Visual check of the wires and connectors.
4 Check and clean the pressure test points.
5 Check the installation pipes for leaks.
6 Visual check of any damage and/or deformation of the following components:
- cylinder/distributor unit;
- flame disc;
- ignition unit;
- flame pipes.
16
Fig. 24
D1143

Advertisement

Table of Contents
loading

This manual is also suitable for:

20082532

Table of Contents