Preparation For Start Up; Combustion Head Adjustment; Ignition Pilot - Riello DB 6 LM C10 TC FS1 A0 T150 Installation, Use And Maintenance Instruction

Oil industrial burner
Hide thumbs Also See for DB 6 LM C10 TC FS1 A0 T150:
Table of Contents

Advertisement

5

Preparation for start up

5.1

Combustion head adjustment

In addition to varying air flow depending on the output requested, the air gate valve servomotor 7)(Fig. 2) by means of a lifting
assembly, varies the setting of the combustion head. This system allows an optimal setting even at a minimum firing rate. For the
same servomotor rotation, combustion head opening can be varied by moving the tie rod onto holes 1-2-3 (Fig. 13).
The choice of the hole (1-2-3) to be used is decided on the basis of diagram in Fig. 14 against the required maximum output.
Setting is pre-arranged in the plant for the maximum run (hole 3).
When dealing with boilers featuring a strong back pressure, if air delivery is insufficient even with the damper fully open, you can
use a different setting to that illustrated in diagram in Fig. 14, do this by moving the tie rod onto the next highest hole numerically
speaking, thus increasing the combustion head's opening and hence air delivery)
N° Hole
3
2
1
0
4000
5.2

Ignition pilot

Make sure that the electrodes are positioned as shown in Fig. 15.
4400
5000
5400
5800
4÷ 4,5mm
D8321
20082173
Fig. 13
6200
6600
7000
7400
Maximum burner output
47
D8417
kW
7800
8200
kW
Fig. 14
Fig. 15
11

Advertisement

Table of Contents
loading

This manual is also suitable for:

20082532

Table of Contents